Sanyo Denki RS2A03A0AL0 Servo Amplifier: Fix Alarm 10 (OC) & 16 (OV)

Page Info

Mason  15 Views  25-11-11  Technical-Guides

Main Content

Sanyo Denki RS2A03A0AL0 Servo Amplifier: Fix Alarm 10 (OC) & 16 (OV)


1. Understanding the Role of the RS2A03A0AL0 in Motion Control Systems

The SANYO DENKI SANMOTION R Advanced Series Servo Amplifier, specifically the RS2A03A0AL0 model, serves as the critical interface between the control system (like a CNC or PLC) and the servo motor. Its primary function is to precisely regulate the voltage and current supplied to the motor windings, ensuring accurate position, speed, and torque control. When an industrial machine experiences an unexpected halt, the immediate display of an alarm code on the RS2A03A0AL0 is the technician's first clue, signaling an internal fault or an external system anomaly that demands rapid resolution to minimize machine downtime.


2. Alarm Code 10: Overcurrent (OC) - Field Diagnostics and Resolution Flow

Alarm Code 10, indicating an Overcurrent (OC) condition, is one of the most common and critical faults encountered with the RS2A03A0AL0. This alarm signifies that the current flowing through the motor or the amplifier's internal circuitry has exceeded its safe limit, protecting the system from catastrophic failure.

2.1. Initial Site Investigation for Overcurrent

When the Overcurrent alarm trips, the field technician must first assess the immediate environment and system components. The technician's experience suggests a diagnostic flowchart based on the severity and context of the alarm:

  • Sudden Alarm on Startup: If the alarm triggers immediately upon power-up or before motion command is given, the issue is highly likely internal to the amplifier or related to a motor phase short.
  • Alarm During Deceleration/High Load: If the alarm occurs during rapid acceleration, deceleration, or under heavy load conditions, the cause is often external, relating to mechanical stress, motor tuning, or poor parameter settings.

2.2. Decision Tree for Troubleshooting Overcurrent (OC)

Check Step Diagnosis Condition Recommended Action (Field Experience)
Motor Cabling Integrity Motor cable insulation shows visible damage or is shorted to ground or phase-to-phase. Disconnect the motor cable from the amplifier. If the alarm still occurs upon power-up, the amplifier may be faulty. If the alarm clears, replace the motor cable.
Motor Condition The motor windings show a short circuit when measured with a megger (insulation resistance tester). If resistance is below acceptable limits (typically <1 MΩ), the motor is likely damaged. Consider replacing the motor.
Load Mechanics The mechanical system is jammed, has excessive friction, or the load inertia significantly exceeds the amplifier’s capacity. Disconnect the motor from the load. If the amplifier runs without the alarm, the issue is mechanical. Check gears, bearings, and lubrication, or reassess the motor/amplifier sizing.
Parameter Tuning High gain settings or aggressive acceleration time constants are configured in the amplifier. Temporarily reduce the velocity loop gain (VP) and acceleration/deceleration time constants. If the alarm clears, fine-tune the parameters gradually.

3. Alarm Code 16: Overvoltage (OV) - Causes and Mitigation Strategies

Alarm Code 16, or Overvoltage (OV), occurs when the DC bus voltage within the RS2A03A0AL0 rises above its safe operational limit. This is most frequently caused by regenerative energy being fed back from the motor to the amplifier, particularly during rapid deceleration of a large inertia load.

3.1. Regenerative Energy and DC Bus Dynamics

When a servo motor is decelerated, it acts as a generator, converting kinetic energy back into electrical energy. This energy flows back to the servo amplifier’s DC bus. If the capacity of the amplifier's internal or external regenerative resistors is insufficient to dissipate this energy as heat, the DC bus voltage spikes, triggering the Overvoltage (OV) alarm (Code 16).

3.2. Practical Solutions for Overvoltage Conditions

The choice of solution depends heavily on the machine's duty cycle and the magnitude of the overshoot:

  • Solution 1: Increasing Deceleration Time: If the machine can tolerate slightly slower operation, increasing the deceleration time constant will reduce the instantaneous rate of energy feedback, often eliminating the OV alarm entirely. This is the simplest fix, provided throughput is not critical.
  • Solution 2: Installing/Upgrading External Regenerative Resistors: For high-throughput machines with high inertia loads, the internal resistor may be insufficient. Field practice dictates checking the resistor usage ratio parameter. If it consistently exceeds 80%, an external regenerative resistor with a higher wattage rating should be installed to increase the dissipation capacity. This shifts the physical load of energy absorption.
  • Solution 3: Checking Input Power and DC Link: The technician should verify that the input line voltage to the drive is within the specified range (e.g., 200V AC ± 10%). An abnormally high input voltage can cause the baseline DC bus voltage to be too close to the OV limit, making even minor regeneration cause a trip.

4. Decoding Less Common, Yet Disruptive Alarms

While OC (10) and OV (16) dominate the field service calls, other codes can signify distinct problems related to the system's integration and control.

4.1. Alarm Code 11: Main Circuit Wiring Error

Alarm 11 is a specific, often perplexing error that points to an issue with the power circuit or control board detection. It typically suggests a fault in the main power circuit where the amplifier detects an abnormal voltage or current path during the pre-charge phase.

  • Diagnostic Approach: Check the main power input connections (L1, L2, L3) to the amplifier for loose terminals or phase loss. If the wiring is correct, the issue often isolates to the amplifier's internal circuitry that monitors the main power status. If the alarm persists despite verified power input, the amplifier itself requires replacement.

4.2. Alarm Code 71: Communication Error (Between Amplifier and Controller)

This alarm signals a disruption in the digital link, commonly a serial bus or fieldbus (like EtherCAT, MECHATROLINK, etc.), used for sending command data and receiving feedback.

  • Diagnostic Approach: The technician must first check the physical layer: examine the communication cables (often shielded twisted pair) for damage, secure connection at both the controller and the RS2A03A0AL0, and verify the correct termination resistors are used on the network. If the physical layer is sound, the focus shifts to the controller's configuration (e.g., node address settings, communication cycle time).

5. Structured Data Reference: Key Specifications and Thresholds

Field engineers rely on rapid access to critical specification data for troubleshooting. The following table provides key operational parameters for the RS2A03A0AL0 model, structured for quick diagnostic reference rather than mere numerical listing.

Specification Aspect Parameter Description Typical Value (RS2A03A0AL0) Operational Context for Troubleshooting
Power Output Rating Maximum continuous output capacity to the motor. 300W (Dependent on motor) Used to confirm if the load requirements of the application exceed the amplifier’s capacity, potentially leading to Alarm 10 (Overcurrent) during peak operation.
Input Power Source Required AC input voltage and phase. Single/Three-Phase 200V AC Directly relates to Alarm 16 (Overvoltage) baseline and Alarm 11 (Main Circuit Wiring Error) detection. Must be stable and within ± 10% tolerance.
DC Bus Overvoltage Trip The internal voltage threshold at which Alarm 16 is triggered. Typically around 400V DC This threshold is crucial for sizing external regenerative resistors. The voltage must never exceed this value during deceleration.
Maximum Peak Current The short-duration current the amplifier can safely deliver. Up to 3 times the rated current Used in tuning. Exceeding this limit even briefly, often due to aggressive acceleration, triggers Alarm 10 (Overcurrent).
Supported Encoder Type Type of feedback device compatible with the amplifier. Serial Absolute Encoder Mismatched encoder types or poor signal quality often result in position errors or motor instability, not primary alarms like 10 or 16, but critical for post-repair testing.

6. Advanced Diagnostic Pathway: Motor & Amplifier Isolation Testing

When Alarm 10 (Overcurrent) or Alarm 16 (Overvoltage) persists, a critical diagnostic step is the isolation of the motor and the amplifier to definitively locate the fault. This is a common practice used by experienced technicians when initial checks fail.

6.1. Procedures for Motor Coil Integrity Check

The technician disconnects the motor power lines (U, V, W) from the RS2A03A0AL0 and performs two key electrical tests on the motor cable side:

  • Phase-to-Phase Resistance: Use a standard multimeter to measure resistance between U-V, V-W, and W-U. The values must be near-identical and typically very low (e.g., <1 Ω). A significant deviation or an open circuit indicates a faulty winding or connection.
  • Phase-to-Ground Insulation Test (Megger Test): Use an insulation resistance tester (megger) to apply a test voltage (e.g., 500V DC) between each phase (U, V, W) and the motor frame ground. The resistance must be very high (typically >100 MΩ). A low reading indicates insulation breakdown, which is a common cause for Alarm 10.

6.2. Procedures for Amplifier Isolation Test

If the motor and its cabling pass all integrity checks, the RS2A03A0AL0 itself is the likely culprit. The isolation test involves:

  • Power-Up Without Motor: The amplifier is powered up with only the control power and main power, but with the motor and I/O connectors deliberately disconnected.
  • Observation: If Alarm 10 or 11 still occurs under no-load conditions and with no motor attached, the internal power stage (IGBTs) or the control logic board of the RS2A03A0AL0 is confirmed to be defective. This decisive test streamlines the replacement process, avoiding unnecessary component swapping.

7. Empirical Guide to System Performance Assessment

A component is not necessarily "fixed" until the machine's performance is verified under real operational stress. Technical experience dictates that the final phase of troubleshooting involves observing the system's behavior, particularly focusing on velocity and position response.

A decision-making flowchart for post-troubleshooting tuning:

  • Condition: If the motor exhibits audible vibration or oscillation during speed command changes.
    • Action: Reduce the Velocity Loop Gain (VP) and increase the Velocity Integral Time Constant (VI). A lower gain reduces the stiffness but increases stability.
  • Condition: If the motor position overshoots the target during rapid moves, followed by a settling period.
    • Action: Increase the Position Loop Gain (PP). A higher gain increases responsiveness but, if too high, will cause Alarm 10 (Overcurrent) by demanding excessive torque.
  • Condition: If the machine experiences frequent Alarm 16 (Overvoltage) during deceleration, despite having the recommended external resistor.
    • Action: Verify the resistance value of the external resistor against the SANYO DENKI specification. If the value is correct, consider decreasing the overall inertia ratio setting if possible, or further increase the deceleration ramp time in the motion controller.

This experience-based approach, moving from definitive electrical checks to nuanced performance tuning, ensures that the resolution of the initial alarm code is robust and durable, preventing recurrence and maintaining high machine reliability. The RS2A03A0AL0, being a high-performance drive, demands this level of attention to detail for optimal operation.


Note to Readers: This article provides general technical guidance for troubleshooting the SANYO DENKI RS2A03A0AL0 Servo Amplifier based on common field experiences. Always refer to the official SANYO DENKI product manual and adhere strictly to all safety procedures when performing diagnostics or maintenance on industrial equipment.